Hey ,
I have R30iB Controller , We have just marked "DO NOT USE" on controller box. But sometimes operator forgets and uses T2 mode . Is there is electrical connection or anything else we can use to disable this function ?
Thank you
Hey ,
I have R30iB Controller , We have just marked "DO NOT USE" on controller box. But sometimes operator forgets and uses T2 mode . Is there is electrical connection or anything else we can use to disable this function ?
Thank you
Didn't find what you were looking for?
New postDear,
You can Replace the switch with dry contacts that selected the mode.
Perform Controlled start ,
See this thread how to perform it ..
https://forum.diy-robotics.com/hc/en-us/community/posts/360055356211-Controlled-start
Then change system variable $SCR_T --> $T2_Lock_Enb ---> 1