After Robotic Maintencance, this alarm appears when I press the blue push button.

Ho my god, it's another bad day for me. Help! :-(
After Robotic Maintencance, this alarm appears when I press the blue push button.

Didn't find what you were looking for?
New postHi There!
As per manual SRVO-157 CHGAL alarm occurs when the capacitor for the condenser voltage of the servo amplifier was not charged within the specified time when the servo power is on.
Source: CONTROLLER MAINTENANCE MANUAL R30IA
Regards,
Hello Rejean, I make a test with new Fanuc Robot R30iB Plus Controller and I have a same error when QF2 Breaker is tripped. This QF2 Breaker is behind Estop Board.
Watch your Breaker.... Good Luck Rejean.

Hi Matthieu, that's right, this QF2 breaker was off. The production line working. Ya HOO !!! :-)
Thank You so much!