Mathieu Berube commented, Hi, If you have the Adapter, the only thing you can do is read the I/O in the robot with a scanner. If you can have the Cognex in scanner mode, you can read the trig I/O in the robot. Otherwise, yo...
-
Mathieu Berube commented, Hi, Are you connected to the E-Stop unit CRMA74?
-
Mathieu Berube commented, Hi, Here's the error description: Internal error. The image cannot be acquired within the time limit. What's your shutter speed?
-
Mathieu Berube commented, Salut Claude, Voici ce que la documentation du CRX-25 donne comme valeurs: Les 3 colonnes sont respectivement J1, J2 et J3
-
Mathieu Berube commented, Hi, Can you show us the procedure?
-
Mathieu Berube commented, Hi, Is the pin 7 and 41 are also jumped from 24V and 0V?
-
Mathieu Berube commented, Hi, Those alarms are related to the same problem. A failure occurred in chain 1 (+24V)/chain2(0V) of emergency stop circuit. There is a possibility that the specification of the teach pendant i...
-
Mathieu Berube commented, Hi, The External Estop is the pin 6 and 40. You need to supply 24V (from the pin 2,3 or 4) to the pin 6 and 0V (from the pin 36,37 or 38) to the pin 40 using the contacts of you estop. The pin 7 an...
-
Mathieu Berube commented, Hi Mathieu, The SRVO-007 is External emergency stop. Be sure that you provide 24V to the pin 24VEXT_IN and that this port is jumped to 24V-2 Same thing with the 0V. Also, be sure to go RES_1CH e...
-
Mathieu Berube commented, Hi, Here's what Fanuc say about this alarm: Check whether the circuitry connected to the dual input signal (SFDI) is faulty. Check whether the timing of the dual input signal (SFDI) satisfies th...