Dear Toby, I can give you an idea about softfloat option. SOFT FLOAT is used in processes to compensate for unexpected variances. Due to occurrences of these variances, Softfloat allows the robot p...
-
Dear toby, I Found this in the knowledge base link also attached: SRVO-062 BZAL alarm (G :x A :x) or SRVO-084 BZAL alarm Encoder batteries have low voltage or the encoder cable is disconnected. ht...
-
Hi laurence, Yes you can! Fanuc sells a plug that you can apply inside of the controller to jumper out the pendant. This allows the Estop circuit to remain ok. and you can use robot without Teach p...
-
Hi Muhammad, INTP-205 is an analog port access error. If you are not using anolog I/O then simply GO TO MENU, I/O and disable the analog I/O.
-
Hi Laurence! You can use FL-NET OPCN-2 (the generic term for a network featuring FA link protocol) interface module. The FA link protocol is intended for the FL-net to be used for data exchange bet...
-
Hi Frankie! As per manual if Servo 0-18 An excessive brake current is detected. The seven-segment LED on the servo amplifier indicates 1. (Action 1) Check the robot connection cable (RM1) and cable...
-
Apologies for misunderstanding the Programming Software with troubleshooting software Please find below Programming Software for GE 90-30 PLC Logicmaster 90-30 is a DOS-based program that runs on ...
-
Hi Toby, You are getting this alarm probably because you haven't set your axis limits properly. This is an OVC alarm, you need to check your axis limit/Set axis limits.
-
Source : FANUC ROBOTICS SYSTEM R-J3 TROUBLESHOOTING AND MAINTENANCE MANUAL